Firefighters normally carry bolt cutters?It is still readily accessible per the definition if it has a standard lock. As far as I know, there is no code restriction on placing a lock on the operationg handle of the emergency disconnect.
The definition of readily accessible does mention keys but then the IN seems to indicate that the intention of a lock wouldn't apply to a residential installation.It is still readily accessible per the definition if it has a standard lock. As far as I know, there is no code restriction on placing a lock on the operating handle of the emergency disconnect.
Accessible, Readily (Readily Accessible). Capable of being
reached quickly for operation, renewal, or inspections without
requiring those to whom ready access is requisite to take
actions such as to use tools (other than keys), to climb over or
under, to remove obstacles, or to resort to portable ladders,
and so forth. (CMP-1)
Informational Note: Use of keys is a common practice under
controlled or supervised conditions and a common alternative
to the ready access requirements under such supervised condi‐
tions as provided elsewhere in the NEC.
If he puts an overcurrent protective device outside, that becomes the service disconnect.Leave the breaker in the panel as a service disco. Unless you want the added work of changing it all up.
Note is not code and there is nothing in the code that can be read as prohibiting locks on the required emergency disconnect. I would never install an exterior disconnect without locking it in the on position.The definition of readily accessible does mention keys but then the IN seems to indicate that the intention of a lock wouldn't apply to a residential installation.
Pretty good chance there is at least one bolt cutter or other tool that can cut said lock in one of the fire trucks when they show up. They don't each individually carry bolt cutters at all times though.Firefighters normally carry bolt cutters?
www.firehosedirect.com
He was already planning on doing that. His question was does he have to change the panel to a main lug panel or can he keep the existing panel. He can keep the existing panel and separate the grounds and neutrals.
Sent from my iPhone using Tapatalk Pro
Sparky, I read your comment as saying the breaker in the panel is still the service disconnect after a breaker has been installed outside. My comment was only saying that the breaker in the panel is no longer a service disconnect.Leave the breaker in the panel as a service disco. Unless you want the added work of changing it all up.
What is the issue with using a meter main. Why would a meter with disco need to be made?I would suspect companies will shortly come up with a meter socket with non fused disconnect, with the appropriate labels. If it was not a "service disconnect" then thats a savings for a retrofit (avoids issues with GEC)
I would guess one reason for installing a meter with a disconnect only is to avoid installing an SER to the main panel location.What is the issue with using a meter main. Why would a meter with disco need to be made?
presuming you are talking about a disconnect ahead of a meter...possibly a lock on both if you can't secure both with a single lock.Would the PoCo lock be on the switch handle, or on the cabinet access hasp?
I'd assume the latter.
Another reason to use a meter with disco is on a upgrade in an older installation with existing 3-wire dryer and range branch circuits.What is the issue with using a meter main. Why would a meter with disco need to be made?
I'm just getting up to speed on this issue, but I would have to argue that 230.85 (3) clearly and explicitly allows for "...circuit breakers on the supply side of each service disconnect..." as long as equipment is SUSE rated.If he puts an overcurrent protective device outside, that becomes the service disconnect.
Putting a breaker outside does NOT necessarily MAKE IT the Service Disconnect, but maybe I'm dreaming....
That's exactly my fear. I'd prefer a non-fusible safety switch so there could be no argument, but the 200A 3R ones get pricey.in the past it kind of did, this new emergency disconnect rule however seems to allow it to not somewhat optional in some cases.
They seem to mostly be interested in being able to interrupt service from outdoors even if it is not a service disconnect.
I can see there being local jurisdictions that end up saying if it contains overcurrent protection that they will consider it to be the service disconnect - NEC doesn't really state that though.
Does that price offset the cost to run the GEC to the new location and/or install an EGC because you are now feeder instead of service conductors?That's exactly my fear. I'd prefer a non-fusible safety switch so there could be no argument, but the 200A 3R ones get pricey.
The cheapest I found a Non-Fusible 200A Gen. Duty Safety Switch for was like $300.00Does that price offset the cost to run the GEC to the new location and/or install an EGC because you are now feeder instead of service conductors?
Maybe somewhat a wash most cases.