Only thing I see is the requirement that an ATS based system must have a generator capable of running the entire calculated load, or else you need automatic load shedding equipment. So you may need a larger generator depending on the NEC code cycle adopted or load shedding or move large non critical circuits to the meter main.
Also wondering how well the grid tie inverter will do with a generator as a source. I'd like to implement something like that myself, but I'm not sure if there are any compatibility issues.
Is the goal to have generator and solar at same time? If so, this is not going to work as the generator can't be used as a source in lieu of the POCO with a grid tie inverter. You would need to have a battery system and charge contoller to do this as the generator can't act as a "battery" the way the POCO source can (voltage and freq. as well as other issues).
You could use this arrangment if you have contacts in the ATS drop out the inverter upon POCO failure.
Texie, Could refer me to some article and etc. that I could read more in detail regarding the
issues you mentioned in your reply.
Thank you
This would be a ggod place to start: http://www2.schneider-electric.com/...:Backup+and+Off-Grid+Systems~!NNM3:Xantrex+XW.
You could also look at sma-america.com.
You need to be looking at off grid systems with generator and utility inputs. These will require battery banks as well. This will get expensive.
There are a lot of things to consider here for what you are proposing. Your present design has fatal flaws (meant gently)
suemarkp
There won't be any load shedding unless you provide it, or unless you're using some generator panel thatincorporates it. A manufacturer's claim that a 13KW generator will "run the whole house" depends a lot on the house. There is no way their claim will work without load shedding or a load calculation. It wouldn't run my house with a 4 ton heat pump, 20KW strip heat, and electric everything else (range, water heater, clothes dryer, swimming pool, multiple refirgerators...).
You need to do a load calculation and see what it comes to. Depending on where this is installed, the NEC as written may or may not apply.
Texie and Suemarkp, Ok how about moving the PV grid tie to Meter / Main dist. panel out side a head of ATS?
Would a battery bank still be required?
I will do a load calc. and will incorporate auto load shedding. is this it ? by moving PV grid tie to M/M sect. and load sheddingrest of proposed install will fly
5) Q. PV system grid tie will be at Panel # 2 in the basement (Load side of ATS)
Would there be any problem if POCO power is lost and GEN and PV both
Supplies power at the same time?
6) Q. What wording needed for labeling to alert fireman that there is more than one
Power source exist?
Texie and Suemarkp, Ok how about moving the PV grid tie to Meter / Main dist. panel out side a head of ATS?
Would a battery bank still be required?
I will do a load calc. and will incorporate auto load shedding. is this it ? by moving PV grid tie to M/M sect. and load sheddingrest of proposed install will fly
Only thing I see is the requirement that an ATS based system must have a generator capable of running the entire calculated load, or else you need automatic load shedding equipment. So you may need a larger generator depending on the NEC code cycle adopted or load shedding or move large non critical circuits to the meter main.
Would you please back this statement up with a code reference? Is this required for residential ATS/generator systems?
I just bid a 400amp service change with an ATS & 17kw generator, due to the actual load, not including AC. Bid clearly stated that if AC would be used during generator usage, a 30KW was needed.
Texie and Suemarkp, Ok how about moving the PV grid tie to Meter / Main dist. panel out side a head of ATS?
Would a battery bank still be required?
I will do a load calc. and will incorporate auto load shedding. is this it ? by moving PV grid tie to M/M sect. and load sheddingrest of proposed install will fly
BTW, I am wondering that ATS wouldn't transfer to generator power, because of seeing voltage generated by PV on its line terminal.
Yes it will because if the POCO fails the PV invertor will shut down because it looses it's utility reference. This is inherent for grid tie invertors.
Sorry texie, I am not following well, but I think what you are saying is that transferring to generator power will not be an issue since invertor will shut down its out put voltage when poco power is lost. Correct?
Correct.