I just got "nailed" by an inspector. I ran a 12/3 Romex to a Washing machine outlet in a laundry room from the panel. I then took a 12/2 to the garage GFCI outlet. Red takes care of the Washer....Black takes care of the Garage. I was written up..."Garage Must Have Designated Circuit". Perhaps I am wrong in assuming that the shared neutral violates the "designated circuit" rule......a rule I can't even find in the codebook. My questions are: Does the NEC require a designated circuit for the garage and does the shared neutral violate a "Designated Circuit description?
Guypowerup. I think the inspector meant to say "Laundry Must Have Designated Circuit."
210.10(C)(2) Laundry Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one additional 20-ampere branch circuit shall be provided
to supply the laundry receptacle outlet(s) required by
210.52(F).
This circuit shall have no other outlets.
Your circuit, even though it has a shared neutral and fed by a double pole circuit breaker, is still
one branch circuit.
Article 100, Definitions.
Branch Circuit. The circuit conductors between the final
overcurrent device protecting the circuit and the outlet(s).
Branch Circuit, Multiwire.
A branch circuit that consists
of two or more ungrounded conductors that have a voltage
between them, and a grounded conductor that has equal
voltage between it and each ungrounded conductor of the
circuit and that is connected to the neutral or grounded
conductor of the system.