Guypowerup. I think the inspector meant to say "Laundry Must Have Designated Circuit."
210.10(C)(2) ... This circuit shall have no other outlets.
Your circuit, even though it has a shared neutral and fed by a double pole circuit breaker, is still one branch circuit.
I'm not following that reasoning at all. If what you're hinting at were a valid read of the code, then I wouldn't be allowed to run a single 12-3 to the kitchen counters and call it a day, because I would have only "one circuit."If we look carefully at the wording of 210.4, it says A multiwire circuit shall be permitted to be considered as multiple circuits. I agree that technically this is no different than running a 12-3 w ground to the kitchen and calling it two circuits.
I think the wording of 210.4 speaks for itself: A multiwire circuit shall be permitted to be considered as multiple circuits. There's no two ways to read that, we have explicit permission to deal with the two lines as as pair of circuits.
Purely design preference. In most commercial applications, where MWBC is most common, what room the lines of a MWBC end up in is usually about #32 on the designer's priority list, IMO.But think about what we are doing when we run such a circuit to the kitchen. We are using the entire circuit for the electrical load in the kitchen, not for other rooms.
Three points for trying, but I don't see the inspector wiggling out from this one.
Most likely the 12-wire looked like a pair of 12-2's, and the inspector was unaware that there were two circuits present.