tryinghard said:
The OP is asking about residential outlets as per their thread name:
Yeah, but in post #18, I said that I was going to assume that his reference to residential was a
mistake because his profile says he's a senior electrical inspector.
tryinghard said:
sminor said:
so would that mean you could put all bedroom outlets on one arc-fault, lights smoke and receptacles?
Yes you can.
Yes you can, except for 210.11(CC)
tryinghard said:
What do you mean by "plug load reduction upfront"?
By "upfront" I mean that there's no residential receptacle load
put in in part 2 so there's no reduction in parts 3 or 4. . For commercial, there's a load added in part 2 [up front] and then a demand factor reduction in parts 3 + 4 [on the back end].
Commercial adds in a 180va [or specific load] in part 2 [220.14(L)]. . Then gives you a demand reduction in part 3 [220.44].
Residential doesn't add a receptacle load in part 2, "No additional load calculations shall be required for such outlets." [220.14(J)]. . And so you don't get the demand reduction in part3 [220.44].
I'm told by people that have done a ton for load calcs that the Optional Method of part 4 almost always gives you the lowest number for
large houses. . I'm sure part of the reason is that 220 lets you "doubledip" for residential part 4 Optional Method. . You get zero for your receptacle load in 220.14(J) and only have to add in the 3va per square foot lighting. . And then you get the "doubledip" in 220.82(B) for the portion of your general load that goes over 10kva.