Brant, without there being a disconnect already in place (as you mentioned) simply tapping the service conductors and installing an outside "main" and having the original inside "main(s)" would be a volation of 230.71 (A) and 230.72 (A)
I was referred from our local Hot Tub retailer to give a price on a Hot Tub installation.
Went to the house, and saw the panel... well part of it anyway... it's a FPE stablock, and it's behind a cabinet.
I told the HO that I will not install anything in the FPE panel, besides, there is not enough room, and even if there were, the panel is only wired for 100A. (Enough experience in this part of town to tell that without looking.)
I told him that I need to upgrade the panel before we install the hot tub.
Anyway, it's a back to back meter / panel setup. The meter has 2" GRC coming up to it on the outside of the house, with the FPE nippled through on the inside of the house.
I told the HO that we cannot put panels behind cabinets anymore (or bathrooms, or kitchens, or on stairs), so the cabinet would have to go, unless he wants to explore putting a WP meter / panel combo. He wants to explore the outdoor option.
So, I went outside, and the deck out back where the meter is, makes the roofline come down to about 7'.
I figured that there is not enough room to put a combo panel / meter on top of the 2" GRC, and not hit the roofline.
I don't want to put a seperate panel to the side, because all the wiring goes directly to the panel, which is directly behind the meter.
Does that make sense?
Any suggestions?
Thanks,
Greg
1st reason: The inspector wants us to bond the GEC to the old panel AND the new panel... I guess the new panel is not sufficient...
3rd reason: The old range wires were too short... so we had to run a splice. No problem... throw a Blue wirenut, and everything is ok... WRONG... the range wiring is AL. So, he wants an AL to AL listed wirenut... well we can't find any... the closest we can find is a CU to AL wirenut and they only go up to #8...
What is the issue here? Am I missing something?
1st reason: The inspector wants us to bond the GEC to the old panel AND the new panel... I guess the new panel is not sufficient...
There is no rule in the NEC that requires bonding to the panel. The bonding is an equipotential bonding if installed outdoors. Bonding grid to the motor not the panel.2nd reason: Bond the Hot Tub motor to the hot tub panel...
I understand that it should be bonded, but that is a UL issue. We did not manufacture the hot tub, and therefore should not be responsible for this.
3rd reason: The old range wires were too short... so we had to run a splice. No problem... throw a Blue wirenut, and everything is ok... WRONG... the range wiring is AL. So, he wants an AL to AL listed wirenut... well we can't find any... the closest we can find is a CU to AL wirenut and they only go up to #8...
What is the issue here? Am I missing something?
I had thought about that, but those are live wires there.
Once I remove the meter, I'm dealing with live, unprotected feeders, straight to the transformer.
Really want to avoid that.
I told the HO that we cannot put panels behind cabinets anymore (or bathrooms, or kitchens, or on stairs), so the cabinet would have to go, unless he wants to explore putting a WP meter / panel combo. He wants to explore the outdoor option.