mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
Ok, yeah I can go along with that. But take a look at 250.30(A) for SDS's. It doesn't say "premises". Then there is 250.142(B). But all that said, part X for over 1KV which "supplements an modifies...."
I still say they need to clarify what they mean by "multigrounded neutral system". I guess one could say that at a transformer bonding everything together and to the neutral and not running a EGC is the only thing it could mean, because any other permutation doesn't make sense.
Perhaps, but when a neutral is mandated to be grounded every 1/4 of a mile and at every transformer, IMHO it becomes obvious as to what they mean by MGN.
If a current carrying conductor is permitted or in this case mandated to be earthed repeatedly, nothing from an electrical theory standpoint says it can not function as a fault clearing conductor.