Per T220-19 (note 3) ranges between 1 3/4 kw and 8 3/4kw, for multiple ranges where some of the ranges falls in column A and B, "the demand factor for each column shall be applied to the appliances for that column and the results added together". As an example: say we have 5 - 3kw and 5-5kw ranges (total of 10) I have been told to take the 3kw's at 62% for 5 ranges and 5kw's at 45% also for 5 ranges then add the 11.25 & 9.3 for a total of 20.55kw. I believe it is more reasonable to use the 10 appliance row, and multiply the 3kw's by 49% and the 5kw's by 34% which would total 7.35 for the 3's and 8.5 for the 5's for a grand total of 15.85kw. It seems to me that the total of the 3's and 5's should be allowed to be at the least equal to 10-5kw's which would derate to 17kw if not less. Please let me know what you think.