TX+ MASTER#4544
- Texas
- electrical Code instructor and mentor
19.55kW is the demand on the service and not a branch circuit.
Dont forget the GFCI breaker.
never heard of that in WA. it was a brand new ckt so shouldnt have any isses with a 4 prong outlet. I got a correction last summer. I haven't heard back from the customer so things must be hunky dory. I do want to just note that every single new range i've seen in years has come wired for a 3 prong outlet for some reason. Then when the installers from Lowes show up they cry about 3 prong outlets needing to be changed to 4 prong! I did net a text from a cat who said my GFI breaker was tripping on his range or dryer or whatever last month plugged into a 4 prong. I told him to remove the factory installed jumper, which he did, and the GFI breaker was happy.
TX+MASTER#4544If initially the range is not compatible with a gfci breaker , I’ll install a standard 2 pole breaker and run the oven for a chemical burn off, and once complete I’ve had positive results with the ranges being compatible with gfci protection . Mass added rule 11 to the mass electrical code . You submit a “gfci unwanted tripping form” to the state and inform the wiring inspector of the issue . And the branch circuit for ranges that prove to be incompatible with gfci protection can be protected by a standard 2 pole breaker (omit gfci protection )
This here is the minimum demand load for the range mentioned in OP.Example: Your range.... 15kW - 12kW = 3 kW x 5% for every additional kilowatt over 12kW per note No.1 of T.220.55
15kW - 12 kW = 3 kW X 5 percent.....3 X .05 = 0.15....or 1.15%
Now, you must increase T.220.55 C column (per the note no. 1) for one 8 kW range from column C and increase it by 1.15 %.
Thus, 8,000 W X 1.15 % = 9200 watts. 9200 watts / 240 volts =38.33 amps,40 amp OCPD.
2023NECThis here is the minimum demand load for the range mentioned in OP.
Can use a 40 or a 50 amp circuit - more of a personal preference as either is code compliant here.
You would have to turn on every element on the thing to see 15 kW of load, won't run for very long before elements begin cycling and reducing overall load at any given point in time, which is a major factor in why they have this set of demand factors for cooking appliances. 15kW is 62.5 amps @ 240V. A 40 amp breaker would hold for a probably several minutes without tripping, but load won't remain at that level indefinitely either. 50 amp breaker would hold even longer at that level.
Why would a 40 amp branch circuit be safer than a 50 amp branch circuit? As long as the conductors are sized correctly what's the difference between the two? The NEC permits either one.The 40 amp breaker is safer.
It is not safer. People who don't know any better might think it is because of the lower rating but the CB is there to protect the conductors, not the appliance.Why would a 40 amp branch circuit be safer than a 50 amp branch circuit? As long as the conductors are sized correctly what's the difference between the two? The NEC permits either one.
A 50 amp breaker would need to have 50 amp conductor.The 40 amp breaker is safer.
2023 NEC TXWhy would a 40 amp branch circuit be safer than a 50 amp branch circuit? As long as the conductors are sized correctly what's the difference between the two? The NEC permits either one.
You've lost me. You said that a 40 amp branch circuit is safer than a 50 amp branch circuit when supplying this range. What does an overload have to do with it? The conductors are protected from overload by the OCPD.2023 NEC TX
For a simple definition of overload, see Article 100 Overload "...........would cause damage or dangerous overheating."
It's safer.
What if he put a 60 amp OCPD on the conductors?
Trust the Code.
TX+MASTER#4544
If the three are wall mounted ovens than No.2023 NEC
Question: Is it permissible per Code to install one 30 amp or one 40 amp or one 50 amp single circuit for up to three electric ovens in a dwelling and treat them as equivalent to one range?
View T. 220.55 and note 6.
Thanks for reading
Comments accepted.
TX+MASTER #4544
Hey, I just said it's SAFER.2023 NEC TX
It's safer.
Trust the Code.
TX+MASTER#4544