19.55kW is the demand on the service and not a branch circuit.
19.55kW is the demand on the service and not a branch circuit.
Dont forget the GFCI breaker.
never heard of that in WA. it was a brand new ckt so shouldnt have any isses with a 4 prong outlet. I got a correction last summer. I haven't heard back from the customer so things must be hunky dory. I do want to just note that every single new range i've seen in years has come wired for a 3 prong outlet for some reason. Then when the installers from Lowes show up they cry about 3 prong outlets needing to be changed to 4 prong! I did net a text from a cat who said my GFI breaker was tripping on his range or dryer or whatever last month plugged into a 4 prong. I told him to remove the factory installed jumper, which he did, and the GFI breaker was happy.
TX+MASTER#4544If initially the range is not compatible with a gfci breaker , I’ll install a standard 2 pole breaker and run the oven for a chemical burn off, and once complete I’ve had positive results with the ranges being compatible with gfci protection . Mass added rule 11 to the mass electrical code . You submit a “gfci unwanted tripping form” to the state and inform the wiring inspector of the issue . And the branch circuit for ranges that prove to be incompatible with gfci protection can be protected by a standard 2 pole breaker (omit gfci protection )