(B) Grounded Conductor Connections.
For existing branch-circuit installations only, if an equipment grounding conductor is not present in the outlet or junction box the frame of the appliance shall be permitted to be connected to the grounded conductor if all the conditions in the following list items 250.140(B)(1), 250.140(B)(2), and 250.140(B)(3) are met and the grounded conductor complies with either list item 250.140(B)(4) or 250.140(B)(5):
The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.
The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum or copper-clad aluminum.
Grounding contacts of receptacles furnished as part of the equipment are bonded to the equipment.
The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.
The grounded conductor is part of a Type SE service-entrance cable that originates in equipment other than a service. The grounded conductor shall be insulated or field covered within the supply enclosure with listed insulating material, such as tape or sleeving to prevent contact of the uninsulated conductor with any normally non-current-carrying metal parts.