Re: Residential service disconnect?
As I said you may have different equipment available in your area.
But around here if you ask for a 400 amp meter socket what you get has a rating of 320 continuous 400 max.
Above that we go to CTs.
This 400/320 socket is accepted around here by inspectors and the utility's for 400 amp OCP.
I have never used one of these with two 200 amp panels but I have used them many times with a single 400 amp OCPD.
If the load exceeds 320 amps for more than 3 hours the 400 amp service is undersized in the first place.
Thanks Roger
Bob