aftershock
Senior Member
- Location
- Memphis, TN
Jim W in Tampa said:aftershock said::shock:
The inspector came out and failed my temporary meter/panel/GFI rec assy. today.
I ran a ground as well as a neutral from the meter socket to the panel. He wants the ground removed. I placed a 1/2" connector at the bottom of the meter center for the bare ground to go through for the ground rod. He wants the connector removed. They run their grounds bare, and I mean without any condiut for the ground rod. :shock:
I scratch my head on this,, but oh well,, I will make corrections as he wants.
More updates as I go along.
He had you remove the ground because it would be a parallel neutral.You only run 1 neutral to panel and bond at panel,after that you seperate neutral and grounds.The other part makes no since
The weatherproof panel below the meter is made of plastic,, that ground was my bond,, so I thought