Is there anything in the installation instructions for placement?
I don't have NFPA72
From Kidde's manual for their i5000 product:
"Smoke alarms should not be installed within 3 ft (.9m) of the following: the
door to a kitchen, the door to a bathroom containing a tub or shower, forced
air supply ducts used for heating or cooling, ceiling or whole house ventilating
fans, or other high air flow areas."
I do agree with the locations, however, (there is always a however in life), "should not" is not the same as "shall not". Can an inspector enforce a recommendation?From Kidde's manual for their i5000 product:
"Smoke alarms should not be installed within 3 ft (.9m) of the following: the
door to a kitchen, the door to a bathroom containing a tub or shower, forced
air supply ducts used for heating or cooling, ceiling or whole house ventilating
fans, or other high air flow areas."
I do agree with the locations, however, (there is always a however in life), "should not" is not the same as "shall not". Can an inspector enforce a recommendation?![]()
I do agree with the locations, however, (there is always a however in life), "should not" is not the same as "shall not". Can an inspector enforce a recommendation?![]()
so, do you think the terminology "forced air supply ducts" refers to all ducts that are part of a forced air system(supply and return) or just the supply ducts?