Re: residential smoke detectors
"1. Has to be installed in accordance with National Electrical Code article 760.
2. Has to be installed in accordance with NFPA 72, National Fire Alarm Code.
3. Has to installed in accordance with NFPA 101, Life Safety Code.
4. If you are using an Uninterruptible Power Supply the UPS must be of the sine wave type, not square wave or quasi sine wave.
So, BRK Electronics must think that we have to use non-power limited fire alarm cable instead of romex. They must somehow think that there is a portion of NFPA 72 that says that a residential smoke alarm is a self contained fire alarm circuit and that interconnected smokes and carbon monoxide detectors must be a fire alarm system.
Now, an Uninterruptible Power Supply also happens to nullify AFCI protection but by the time that I stick in a hard-wired UPS I might as well put in a commercial grade fire alarm system.
Guess that I will have to try to find NFPA 72 over at the library or borrow a copy from somebody for a few weeks."
Your last statement is very appropriate for contractors today. The manufacturers are pushing as much of the responsibility to the contractors as they can and this has changed, and will continue to change contracting as we knew it.
Instead of throwing the instructions away before reading them, we now have to read them or weap.