Hi,
Can you use a braker lock off " breaker is not within sight" as a disco within sight for a resi spa tub?
 
No I don't see that option


680.12 Maintenance Disconnecting Means.
One or more means to simultaneously disconnect all ungrounded conductors
shall be provided for all utilization equipment other
than lighting. Each means shall be readily accessible and
within sight from its equipment and shall be located at least
1.5 m (5 ft) horizontally from the inside walls of a pool,
spa, or hot tub unless separated from the open water by a
permanently installed barrier that provides a 1.5 m (5 ft)
reach path or greater. This horizontal distance is to be measured
from the water’s edge along the shortest path required to reach the disconnect.

 