Don't know what app you have, probably ok though. There is a downloadable spreadsheet on Mike Holts main website under "free stuff" IIRC. I think that is somewhat widespread recognized tool to use. You can rename and save for each project you do for your records. If you don't have Microsoft Office it does work in the free "Open office"
Below are screen snips of it using figures I mentioned in a previous post in this thread. It does allow you to figure available current from the source (assuming infinite primary ability) by entering kVA and impedance, or if you already have a known starting fault current level you can plug it in instead.
It has spaces on the sheet for next two levels downstream, say a subpanel then a branch circuit. Need more levels start a new sheet with available current at starting point at the utility fault current portion at top of the page.
View attachment 2554622View attachment 2554623View attachment 2554624
Notice how on this one L-N available current was higher than L_L at the service (mostly because of short length of conductors) but as we got further away not only did both L-N and L-L get lower but L-N did become less than L-L.
2% impedance I have there probably typically will be higher in the field on a 50 KVA transformer, but not necessarily a lot higher. 25's and 37.5's is somewhat safe to assume they will be near 2.0% worst case some will be higher.