Is a refrigerator (a standard kitchen one) receptacle usually on its own circuit? Or is it connected to the counter top receptacle circuits (i.e. small appliance branch circuits)?
I usually assume the refrigerator load is included in the two 1500A small appliance branch circuits for my calculations. I also do the same with microwaves.
I use 220.30 (the optional method) to do my calcs. 220.30 (B) (3) has me wondering. It says "... the nameplate rating of all appliances that are fastened in place, permanetly connected, or located to be on a specific circuit..." need to be included in the calcs.
If thats the case, and I connect the refrigerator to its own circuit, then do I now need to include it in my calcs? But if its on the same circuit the counter top receptacles then I don't have to include it in the calcs?
I usually put the dishwasher and disposal on their own seperate circuits and I include them seperately in my calcs.
Another question I have is about the HVAC loads. Assuming the residential design work I do has a heat pump split system with an air handling unit (usually w/aux. electric heat) and an outdoor condensing unit. I have been including the loads from both the AHU and the CU at 100% in my calcs. I'm not sure that this is right. I'm not sure about the operation of the split system and whether both the AHU and the CU will operate simultaneously.
I usually assume the refrigerator load is included in the two 1500A small appliance branch circuits for my calculations. I also do the same with microwaves.
I use 220.30 (the optional method) to do my calcs. 220.30 (B) (3) has me wondering. It says "... the nameplate rating of all appliances that are fastened in place, permanetly connected, or located to be on a specific circuit..." need to be included in the calcs.
If thats the case, and I connect the refrigerator to its own circuit, then do I now need to include it in my calcs? But if its on the same circuit the counter top receptacles then I don't have to include it in the calcs?
I usually put the dishwasher and disposal on their own seperate circuits and I include them seperately in my calcs.
Another question I have is about the HVAC loads. Assuming the residential design work I do has a heat pump split system with an air handling unit (usually w/aux. electric heat) and an outdoor condensing unit. I have been including the loads from both the AHU and the CU at 100% in my calcs. I'm not sure that this is right. I'm not sure about the operation of the split system and whether both the AHU and the CU will operate simultaneously.