CAN A GAS CLOTHE DRYER BE FED FROM THE WASHER C RCUIT ?![]()
210.11(C)(2) Is for the required laundry branch circuit. It references 210.52(F) which requires at least one receptacle outlet for the laundry on a 20 amp circuit. No where in either section is the combined motor load, or for that matter, any load mentioned.Wiuldn`t you have to take the combined motor load int consideration ?
What about the section that states that if the connected equipment used more than 50% of the circuit's ampacity, it has to be a dedicated circuit? I don't know what clothes washers typically draw, off hand.Originally posted by infinity:
210.11(C)(2) Is for the required laundry branch circuit. It references 210.52(F) which requires at least one receptacle outlet for the laundry on a 20 amp circuit. No where in either section is the combined motor load, or for that matter, any load mentioned.Wiuldn`t you have to take the combined motor load int consideration ?
Does this section apply to cord and plug connected motor driven appliances?What about 430.53 would this apply ?
mdshunk,Originally posted by mdshunk :
What about the section that states that if the connected equipment used more than 50% of the circuit's ampacity, it has to be a dedicated circuit? I don't know what clothes washers typically draw, off hand.