Resistor For 110V

Status
Not open for further replies.

learning101

Always learning
Location
Arizona
Occupation
Electrician
If the supplied voltage to an LED indicator light is 120VAC but the light is rated for 110V, is a resistor needed for the longevity of the LED?
 

paulengr

Senior Member
If the supplied voltage to an LED indicator light is 120VAC but the light is rated for 110V, is a resistor needed for the longevity of the LED?

An LED has a current limit, not voltage. Drivers regulate current. So if you just had a naked LED with no driver you most certainly need a resistor but that’s a terrible way to do things because the LED will end up pulsed DC, off for half a cycle, and variable output. And your control is limited…high power LEDs exhibit some negative resistance and tend to go into thermal runaway. That’s what the driver circuit does.

So if you have a light fixture, no. If you have just the LED (no driver) then yes.
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
If the supplied voltage to an LED indicator light is 120VAC but the light is rated for 110V, is a resistor needed for the longevity of the LED?
FWIW we 110Vac for our control systems for things like indicator lights. We used back to back LEDs.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
If the supplied voltage to an LED indicator light is 120VAC but the light is rated for 110V, is a resistor needed for the longevity of the LED?
A better way to put this is that pilot lights that use LEDs have EITHER what's called a "driver" for them, a little printed circuit board that takes in the AC control circuit power and uses a Switch Mode Power Supply circuit to provide low voltage DC to the LED, or a cheap simple circuit consisting of a diode and a dropping resistor, MAYBE a capacitor to smooth out the pulsing DC through the diode.. MOST of those have a fairly wide voltage input range to where 120V would be acceptable. But "your mileage may vary", meaning we don't know WHAT you have and what its specs are.
 

learning101

Always learning
Location
Arizona
Occupation
Electrician
Below is a link to the part that I'm going to use in an electrical design---see attachment. If a resistor is required to go from 120v down to 110v, I'd assume the resistor would go in-between the load and the part contact?

EPO Push/Pull Button
 

Attachments

  • Pool Equipment Electrical Control Design.pdf
    546.4 KB · Views: 9

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I believe anything rated at 110v is intended to be supplied by 120v without needing a resistor, unless the manufacturer says otherwise, in which case they should also specify a value for it.
 

paulengr

Senior Member
I believe anything rated at 110v is intended to be supplied by 120v without needing a resistor, unless the manufacturer says otherwise, in which case they should also specify a value for it.

“Standard conditions” with UL and NEMA is nominal voltage +10/-15%. The supply voltage is 120 V so you are allowed 5% voltage drop so the load rating is 110 V nominal. But this is all nominal. It should handle anything between 94 and 121 V.
 

learning101

Always learning
Location
Arizona
Occupation
Electrician
Thank you so much to everybody that responded! Absolutely helpful and quite informative reading the responses!!

-Jake
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
LED's are usually at full brightness with only a couple of volts or less.
Any LED rated for 110 V has to have a series resistor inside the package, or something else to limit the current and to drop 99% of the voltage.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
LED's are usually at full brightness with only a couple of volts or less.
Any LED rated for 110 V has to have a series resistor inside the package, or something else to limit the current and to drop 99% of the voltage.
Many lighting (not so much indicator) LED bulbs avoid much of the energy waste by stacking multiple junctions in series.
And it is more like 97% for a single junction. :)
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Many lighting (not so much indicator) LED bulbs avoid much of the energy waste by stacking multiple junctions in series.
And it is more like 97% for a single junction. :)
Well, yeah. Anything like a typical LED lamp isn't just going to use a resistor to drop 99% (or 97% whatever it happens to be for that particular LED) of the input voltage.

That would be less than 3% efficient before even thinking about the LED efficiency.

And he did say 'indicator light", so I don't think we are talking about typical ambient light fixtures.

I always spec. transformer driven LED's for pilot lights. They cost a little more, and I'm not worried about efficiency, but it just seems like they last longer.
 

topgone

Senior Member
Well, yeah. Anything like a typical LED lamp isn't just going to use a resistor to drop 99% (or 97% whatever it happens to be for that particular LED) of the input voltage.

That would be less than 3% efficient before even thinking about the LED efficiency.

And he did say 'indicator light", so I don't think we are talking about typical ambient light fixtures.

I always spec. transformer driven LED's for pilot lights. They cost a little more, and I'm not worried about efficiency, but it just seems like they last longer.
And to think the voltage is not going up as you go down the line!
 