This is to request advice in using a three phase breaker for a single phase circuit
1. The Outdoor panel on the left is 120/208 VAC and is fed from a 3 phase Square D I Line Panel 700' away.
2. We need to replace the Outdoor panel because because its outdated and has Two Hots and a Neutral but no Equipment Grounding Conductor.
3. We only need single phase 120 VAC 40 A service at the Outdoor panel. (One Hot, One Neutral, One Ground)
4. Can I make things right by re-purposing the 120/208 2H and 1N conductors as 120 1H, 1N, 1G conductors and reconnecting them to one pole of a 3 phase breaker?
So my question is :
1. If I find an I Line circuit breaker that is phased A-C, can I only use phase A on that breaker? ( we only need 120 VAC)
2. More importantly, can we take the two hot and one neutral conductors and re purpose them as one Hot, one neutral and one ground inside the I-Line Feed Panel?
Thanks in advance
Respectfully
Installer

1. The Outdoor panel on the left is 120/208 VAC and is fed from a 3 phase Square D I Line Panel 700' away.
2. We need to replace the Outdoor panel because because its outdated and has Two Hots and a Neutral but no Equipment Grounding Conductor.
3. We only need single phase 120 VAC 40 A service at the Outdoor panel. (One Hot, One Neutral, One Ground)
4. Can I make things right by re-purposing the 120/208 2H and 1N conductors as 120 1H, 1N, 1G conductors and reconnecting them to one pole of a 3 phase breaker?
- Using a Three Phase breaker as a Single phase 2 Pole breaker has been discussed numerous times on this Forum https://forums.mikeholt.com/showthread.php?t=156758
- The Schneider website says: https://www.schneider-electric.us/en/faqs/FA87496/
So my question is :
1. If I find an I Line circuit breaker that is phased A-C, can I only use phase A on that breaker? ( we only need 120 VAC)
2. More importantly, can we take the two hot and one neutral conductors and re purpose them as one Hot, one neutral and one ground inside the I-Line Feed Panel?
Thanks in advance
Respectfully
Installer

Attachments