Question that was sent
All of these conduits contain over three current-carrying conductors. According to NEC Table 310.15(c)(1), derating must be applied, which affects the ampacities of the conductors. As a result, the conductors may not be adequately protected by their corrected ampacities.
For example, Conduit AC-MCC contains 18 current-carrying conductors. This results in a derated ampacity of only 15 amperes for #12 AWG conductors, due to a 50% correction factor. Consequently, these conductors cannot be protected by a 20-amp OCPD.
Reply below
The calculated load for each of the heat trace circuits was a 15A continuous load. The conductors are sized correctly to carry the anticipated H/T load, even with the 310.15(C)(1) derating factor taken into account. Although the conductors have a calculated ampacity of 15A, a 20A OCPD is permitted. Section 240.4(B) permits the use of the next higher standard rating of OCPD. This also checks out based on 210.20(A) given that a 15A continuous load would require a 20A OCPD.
All of these conduits contain over three current-carrying conductors. According to NEC Table 310.15(c)(1), derating must be applied, which affects the ampacities of the conductors. As a result, the conductors may not be adequately protected by their corrected ampacities.
For example, Conduit AC-MCC contains 18 current-carrying conductors. This results in a derated ampacity of only 15 amperes for #12 AWG conductors, due to a 50% correction factor. Consequently, these conductors cannot be protected by a 20-amp OCPD.
Reply below
The calculated load for each of the heat trace circuits was a 15A continuous load. The conductors are sized correctly to carry the anticipated H/T load, even with the 310.15(C)(1) derating factor taken into account. Although the conductors have a calculated ampacity of 15A, a 20A OCPD is permitted. Section 240.4(B) permits the use of the next higher standard rating of OCPD. This also checks out based on 210.20(A) given that a 15A continuous load would require a 20A OCPD.