jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
Nobody said a 20A breaker can't be used. But not with 12awg wire derated that much. If the circuits can use 15A breakers then the wire is fine. If the circuits require 20A breakers then they need larger wire or an arrangement with less of a derating factor.I understand why a 20 amp wire can't be used because of derating of course, but why can't a 20 amp breaker be used for each heat trace? Maybe I'm missing something