M masterintn Member Location southeast Aug 27, 2019 #1 If retrofitting T8 fluorescent fixtures can you use the small conductors existing in the fixture to connect to line voltage?
If retrofitting T8 fluorescent fixtures can you use the small conductors existing in the fixture to connect to line voltage?
kwired Electron manager Location NE Nebraska Occupation EC Aug 27, 2019 #2 to supply that particular luminaire yes, say you had a continuous row or other daisy chained luminaires, you can't carry the branch circuit on through the luminaire with those "fixture taps"
to supply that particular luminaire yes, say you had a continuous row or other daisy chained luminaires, you can't carry the branch circuit on through the luminaire with those "fixture taps"