If someone were to say that conductors cannot be reused (nobody's said that so far), they would also be saying that something fundamentally in the installation or reinstallation process damages conductors. If we were to belive that, the whole wired world is in a world of hurt. The same care that was taken to install the conductors originally can be taken in their removal. The conductors can also be re-installed with that same high level of care. I've reused many a conductor (particularly larger than #4), whether energized previously or not, I can attest that it is a sound practice. I would reiterate the suggestion that the conductors be meg'd. Meg them before removal from the old raceway, and meg them again after they're reinstalled in the new location.
That's not how you remove conductors. That's how you install them.Meg em especially after they are half hitched a bunch of times and pulled out with an old Ford F150. LOL.
JJ
Of course not, but that's a requirement of sound electrical contracting.Even if conductors were removed and reinstalled I find no provision of the NEC that would require them to be megger tested. Does such a provision exist?
110.7 Requires one to install conductors without short circuits, ground faults, or any connections to ground...
That is what inspectors may reference to request meggering.
IMO that's very weak and unenforceable. You could say that about any conductor in a conduit.
Yeah, but if I pulled in some medium voltage cable, would you throw the switch without testing? Heck, even 480 can make a mess.IMO that's very weak and unenforceable. You could say that about any conductor in a conduit.
I know you're only joking, but stories abound of conductors that lasted for a short while, without being tested, after the breaker was turned on. Could be days, weeks, or months, but without testing you have no idea where you stand. The breaker might be on the razor's edge of a ground fault.True, but most conductors are tested when the CB is turned on for the first time. If there's a problem you'll know then.![]()