I need some help understanding a ground fault on this transformers secondary. I don't deal with 480/277-2300 transformers often.
I will attach the name plate info and a few pictures. This transformer is being reverse fed. It's stepping up 480/277 to 2300V in what I believe is an ungrounded delta secondary. I did confirm from the manufacturer that the delta isn't corner grounded internally. The mfg engineer couldn't answer my specific questions because he said he's not a power systems eng.
The 2300V secondary travels about 1500' on a steel bridge to a switch (I think) and steps down to 480/277V
The primary feed is 3 phase 4 wire 480/277. The neutral lands on the XO and has a bonding jumper strap to the enclosure, which is tied in to ground rods.
The secondary has 3 medium voltage cables going into conduit with a green #4 thhn conductor. (I think this is acting like the equipment ground?) but the #4 thhn is also bonded to the enclosure.
Does this transformer need ground fault monitoring on the secondary for unintentional ground?
If a phase unintentionally goes to steel, will the 2.3kV comes back via egc to the enclosure, which the 480/277 neutral is tied to, does it put 2300V on the gear, and is it rated for that voltage, or will the primary protection open?
Does the primary even need this neutral?
Thanks
I will attach the name plate info and a few pictures. This transformer is being reverse fed. It's stepping up 480/277 to 2300V in what I believe is an ungrounded delta secondary. I did confirm from the manufacturer that the delta isn't corner grounded internally. The mfg engineer couldn't answer my specific questions because he said he's not a power systems eng.
The 2300V secondary travels about 1500' on a steel bridge to a switch (I think) and steps down to 480/277V
The primary feed is 3 phase 4 wire 480/277. The neutral lands on the XO and has a bonding jumper strap to the enclosure, which is tied in to ground rods.
The secondary has 3 medium voltage cables going into conduit with a green #4 thhn conductor. (I think this is acting like the equipment ground?) but the #4 thhn is also bonded to the enclosure.
Does this transformer need ground fault monitoring on the secondary for unintentional ground?
If a phase unintentionally goes to steel, will the 2.3kV comes back via egc to the enclosure, which the 480/277 neutral is tied to, does it put 2300V on the gear, and is it rated for that voltage, or will the primary protection open?
Does the primary even need this neutral?
Thanks