Pretty much all the banks here are Y primary built out of one bushing transformers the MGN must connect to the neutral of the primary if that is the case
Secondary side can be wye or delta - depends on what service is being supplied, and of course either setting taps or using right transformer to get desired secondary voltage.
Open delta systems are fairly common around here as well, the primary side of those banks are two phase conductors again connected to single bushing transformers and MGN connects as well - so you have an "open wye" so to speak for the primary side.
You don't see two bushing transformers around here, if you do it is probably some older setup, they don't use anything but single bushing transformers for pole mounted transformers.
So, you have actually seen a Y Primary (all four leads connected - not "open Y") and Delta Secondary (not "open D)? Could be, but I don't know of any reason why one would want to do this.
I'm definitely out of my area of expertise and I rarely ever work with separate single phase transformers - all I've seen were pretty small, a few hundred KVA or less. Been staring at this stuff a lot of years, still, lots of stuff out there I haven't seen.
Now, back to the OP case:
I've never heard of a common core deliberately connected as a 4WY primary-closed D secondary.