Thanks, cf....
One question. You mentioned load as a deciding factor, but would 368.17 not require the OCP not to exceed the buss rating. If both transformers can feed the buss simultaneously, it would appear to be a violation of 368.17 ..............
Sorry for ignoring you - (What foolishness - no I'm not. The sun is out, summer is here. Kid and I are building a tree house. Wife and I are planting shrubs. Life just doesn't get much better.
)
But back to this. I'm not sure. I've never put in or worked a double ended sub that did not have a tie CB. And, all I have here is a 2005 NEC. So you will have to tell me if that changed.
Also, does 368 apply? Is this a busway or a switchboard?
If 368 does apply, look at 368.17, ex2, which sends you to 450.6.A.3. Also see 450.6.A.4.
As I mentioned, I've never put one in with out a tie CB, but it appears the NEC allows the load to be limited by design.
cf