chris kennedy said:Where would you pick up an EGC for the secondary? Could you use the primary EGC?
Even an ungrounded delta system must be connected to the buildings grounding electrode system.
See 250.30(B) for transformers or 250.24(E) for services.
Beyond that all the normal EGC requirements apply.