Reversed polarity receptacles

Status
Not open for further replies.

lady sparks lover

Senior Member
I'm not sure what this is or what it means, but I figured who better to ask then all the intelligent men and women of this site. Can someone explain what they are and what they do. Also why they are installed? :)
 
Re: Reversed polarity receptacles

Afternoon lady,
I've been sitting here looking at your post,maybe as others have..Reversed polarity on a receptacle device.Is the ungrounded,and the grounded connection of wires to prespective identified terminals,reversed in field.
 
Re: Reversed polarity receptacles

What would a male plug configured as an inlet to a piece of equipment be called? Could that be what is described.

In other words a male connector but not on a cord, instead fixed in a recessed socket attached to equipment meant to be supplied by a separate cord.

Jim
 
Re: Reversed polarity receptacles

Jersey,
It's not a utter.-Grin'in-Reading you post sir,you may haved descibed a recessed mount pin-sleeve device.You might find it at leviton Products site.Or it may be a recessed single receptacle to power the unit/equipment that it's installed on..

[ April 04, 2005, 02:26 PM: Message edited by: dillon3c ]
 
Re: Reversed polarity receptacles

In other words a male connector but not on a cord, instead fixed in a recessed socket attached to equipment meant to be supplied by a separate cord.
That would be a "flanged inlet".
 
Re: Reversed polarity receptacles

Its also known as a motor base plug. A flanged inlet is commonly used at a building to plug a generator cord into (female on cord, male at building)
 
Re: Reversed polarity receptacles

If you are talking about the actual term "reversed polarity", it is most often used to describe a device that is incorrectly wired.
With 120V., it is when the grounded conductor is connected to the "brass-colored" screw & the ungrounded conductor is connected to the "white/silver- colored" screw.

As don_r says, there is a flanged inlet.
 
Re: Reversed polarity receptacles

Correct, kiloamp7! The "gender" of a connector should not be confused with the "polarity" of its individual conductors.
 
Re: Reversed polarity receptacles

I did not say anything about the polarity of conductors..I said the grounded and ungrounded conductors, to there respected terminals are reversed in the field.

[ April 05, 2005, 10:38 AM: Message edited by: dillon3c ]
 
Re: Reversed polarity receptacles

Originally posted by dillon3c:
I did not say anything about the polarity of conductors..I said the grounded and ungrounded conductors, to there respected terminals are reversed in the field.
Well dillon, that is what polarity is all about isn't it? Aren't the grounded and ungrounded conductors individual conductors which are sometimes reversed but not on purpose I hope.

I am saying let's not confuse gender with polarity.
 
Re: Reversed polarity receptacles

No grounded conductor shall be attached to any terminal or lead so as to reverse the designated polarity.Rattus does this statement suit you?
 
Re: Reversed polarity receptacles

Originally posted by dillon3c:
I did not say anything about the polarity of conductors..I said the grounded and ungrounded conductors, to there respected terminals are reversed in the field.
Wow, thanks for answering...

Ok, so What's the big deal? So the hot is connected to the neutral terminal, and the neutral is connected to the hot, correct?? Ok..I get it....

Other than it being wrong, will it cause a safety issue?

Lady :)
 
Re: Reversed polarity receptacles

It could cause safety issues yes.Should a lamp be pluged in you now made the shell hot.There are also some equipment that might have surge protecters that could fry.
 
Re: Reversed polarity receptacles

Originally posted by dillon3c:
No grounded conductor shall be attached to any terminal or lead so as to reverse the designated polarity.Rattus does this statement suit you?
No problem dillon. All I am saying is that we should not confuse polarity and gender as some have done.
 
Re: Reversed polarity receptacles

Reversing the polarity can be lethal to electronic equipment. Polarity is a proper design feature of equipment.
 
Re: Reversed polarity receptacles

Reversing the polarity can be lethal to electronic equipment. Polarity is a proper design feature of equipment.
Maybe if it was DC device on a Dc circuit?
On an AC system there is no real reverse polarity as far as the positive or negative, as they interchange 60 times a second.

But from a safety stand point there can be problems with old TV's that reference the grounded conductor to there case, Shell's of lamp holders, and many other items that could have the polarized blade (wide one) used as the grounding conductor. Another problem I have run into is when a DYS boot legs a ground off a neutral and the hot and neutral was switched at another junction box! :eek: This allows everything that gets grounded by these plugs to have a 120 volt potential on the grounding (like a freezer in a garage) to Earth which could be lethal.
 
Re: Reversed polarity receptacles

LSL: in modern grounded systems, where the neutral is bonded to the grounding electrode system, reversed polarity can be lethal.

it is not a matter of the polarity reversing on the neutral. notice that on most distribution lines the neutral is bare. it has no potential to ground in whatever state it is in. the obverse is also true. the hot is always in some potential to ground.

double insulated drills, for example are not a danger, and it doesn't matter which of the tines of a plug are joined in a receptacle. but take the example of a light and socket. in a correct system, the shell will not shock, even with the light on. however reverse the polarity and touch the shell and you will discover with an intimacy not soon forgotten exactly how conductive household materials are.

there are numerous places where reversed polarity can be life threatening. it is dangerous and against the NEC.

paul :cool:

[ April 06, 2005, 02:06 AM: Message edited by: apauling ]
 
Re: Reversed polarity receptacles

Wayne, yes, "polarity" is a bit of a misnomer in AC systems, but we all know what it means, I hope.

Paul, I don't believe the shell of a lamp socket contacts either conductor, not on purpose anyway. And, in the days before polarized connectors, polarity could be either way, and no one cared. I can't think of any case where reverse polarity would be a hazard to humans or equipment, but I don't know everything yet.

Should be done right though.
 
Re: Reversed polarity receptacles

Rattus,
Originally posted by rattus:

Paul, I don't believe the shell of a lamp socket contacts either conductor, not on purpose anyway.
it has to contact a conductor for the lamp to work, for the code requirement of which conductor it contacts see 410.23

Roger
 