I've been wiring houses as of the past few years and have not done any commercial,industrial in a while...
Through a friend it looks like I'm wiring a new restaurant to be installed in an existing strip mall.
Looking at the prints, things don't look right. Am I out in left field or did the engineer put something together that the electrician has to re engineer to make it right..
I'm confused with the 200 a feeding the 75 kva transformer from panel HP. (at 90 amps can it be protected at 200+%)
The 200 amp disconnect feeding the two 120-208 volt panels ??? should that not be there and instead go to a trough to to main breaker panels??
The load of the two LV panels..is that too much for that transformer...??
Do the numbers and diagrams look right or is it me??