Review - Qwik-Grip and other SqD panel features

Status
Not open for further replies.

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
I almost always use another brand for panel changes, but I recently did a panel change using a Square D HomeLine panel with Qwik-Grip. I've been wanting to try Qwik-Grip for a while and finally got a job where I thought it would work well.

Qwik-Grip brochure: https://www.schneider-electric.us/e...53jxHi0dQVdF6SBcGGysTT75DdUnngcBoCiLsQAvD_BwE

Qwik-Grip is more complex than it first appears. They give you a map of where the various sized cables can go. Some spaces are too small for larger cables so you have to do a little pre-planning on the order you land cables. For example, the furthest back space in each slot can only handle a 14-2.

The max cable size is 10-3. So you still have to use KO's and connectors for larger cables. Note that there are only four 1/2" to 3/4" KO's and one 1" to 2" KO on each end of the panel since the Qwik-Grip takes up most of the space.

The job I was doing had a few newer NM cables and a lot of old cloth covered NM. While the newer NM slid right in each slot, the older NM was sticky (probably due to the rubber inside deteriorating) and didn't want to slide very well. It also seemed a bit thicker which didn't help. I ended up using a blunt tipped tool to gingerly force the cables into the slots.

Overall, I'd say the Qwik-Grip did save time and effort and I will be using it again.

Comments about other SqD features:

Changeable main breaker - This particular job required 150 amp panel now and the ability to upgrade to 200 amps later. The SqD panel made this easy. I purchased a 200 amp load center and a separate 150 amp main breaker (both of which were available at the Lowe's big box store) and swapped the main in a couple of minutes. I'll use the 200 on another job by purchasing a MLO panel. The only reason I did it this way was because I wasn't sure the 150 amp MB panels were rated for 200 amps although I thought they probably were. Another nicety is the main breakers fits both Homeline and QO panels.

Twin breakers - Every slot on the panel allowed twins and the twins are just slightly more expensive than two single breakers. The panel I installed was a 30 slot/60 circuit. This is a feature of HomeLine panels. QO panels don't allow this.

Full length neutral bars - These were an unexpected help. Being able to land neutrals and grounds the full length of the panel made the installation look neater and there was more room to land them. I didn't have any plug-on neutral devices to install, but I can see where that would be a benefit also.

Cover twistouts - This was my only complaint with the SqD panel. The cover twistouts did not come out cleanly. They left little tabs of metal which hit the breakers and interfered with the cover sitting flat. There wasn't a good way to remove them other than filing.
 
Last edited:
Thank you for the review. It is interesting that you had problems with the dead front knockouts, that's the one thing I didn't have problems with on the last Square D 200 amp panel I put in a house. All of the half inch knockouts were easy to remove though the larger one for an 80 amp circuit to a subpanel, I wound up inadvertently busting out the next size up ring from what I needed, requiring a reducing washer. Also none of the holes on either neutral bar are large enough to accommodate such wire (was Al SE Cable), requiring a rather flimsy looking one screw add-on lug. I'd think at least two holes on the neutral bar could accommodate larger than #4 wire.

Are there optional slide in inserts that can accommodate larger cable? How much time did you lose filing off those tabs?
 
While many of the twistouts left some remnant of metal, two slots were bad enough to require filing. After I found my file buried at the bottom of my tool bag, it took just a few minutes to clear up the problem. However, these few minutes were at the end of a long day so I would have preferred to not be doing it.

Not sure if SqD make inserts for larger wires. I have some made by GE that I use on all panel brands. Probably the only GE product I voluntarily purchase.
 
Have you considered using the Square D retrofit Homeline loadcenters?

The cover is a few inches longer than the can so you can cut out the wall making it easier to get the new can in place. And it has large rectangular KO’s in each corner to bring the cables in.

Thanks for the review though. I’m ordering some of the quik-grip loadcenters in a couple of weeks for a new resi project.


Sent from my iPhone using Tapatalk
 
Have you considered using the Square D retrofit Homeline loadcenters?

I haven't seen SqD's retrofit line yet. I keep looking for opportunities to use Eaton's retrofits, but it hasn't worked out. The last panel I went to look at with retrofits in mind turned out to be so rusted, the can was useless and needed to be replaced. Before that I had two identical condo panels I wanted to retrofit, but it turned out Eaton did not make guts that would fit the 11" wide can.
 
We use Homeline exclusively for all new construction and service upgrades/panel changes. I haven't tried the QuickGrip yet but a few of the rough-in crews have, and so far they like it.
 
We just switched from using GE to Sq. D Homeline. Time will tell if we have more issues with the AFCI circuit breakers.
 
re: two slots were bad enough to require filing

- keep a cheap $7 HF step drill in elec toolbox for just such events. Also are great for new holes. Beats filing, can ream off a burr with just a twit of the drill with pliers.
 