1.) NEC Section/Paragraph: 406.3(D)
2.) Proposal Recommends: [revised text]
3.) Proposal: 406.3(D) currently reads:
But there contains no language, permissive or otherwise, in relation to additions to existing circuits.
Users of the code looking to 250.130(C) when installing an addition to an existing circuit are advised by the FPN to see 406.3(D), but are left empty-handed when they get there.
The section in question (406.3(D)) effectively bends the standard requirements for new installations to provide relief for the installer when dealing with old work. Given the leniency put forth by this section regarding replacement receptacles, it appears that old 2-wire installations, while regretable, do not present an "imminent danger to occupants" as stated in 80.5(B).
80.5(C) expresses that "Additions...shall not cause a building to become unsafe..." By expressing explicit guidelines for additions to existing circuits, installers will be forbidden to connect an unbonded EGC between receptacles, decreasing the shock hazard in the event of an unbonded fault.
Whether accepted or declined, I hope this proposal causes the panel to adopt some definute wording, to fill the void on existing installations.
[ June 26, 2005, 11:36 AM: Message edited by: georgestolz ]
2.) Proposal Recommends: [revised text]
3.) Proposal: 406.3(D) currently reads:
Revise text:(D) Replacements. Replacement of receptacles shall comply with 406.3(D)(1), (2), and (3) as applicable.
(1) Grounding-Type Receptacles. Where a grounding means exists in the receptacle enclosure or a grounding conductor is installed in accordance with 250.130(C), grounding-type receptacles shall be used and shall be connected to the grounding conductor in accordance with 406.3(C) or 250.130(C).
(2) Ground-Fault Circuit Interrupters. Ground-fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.
(3) Nongrounding-Type Receptacles. Where grounding means does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).
(a) A nongrounding-type receptacle(s) shall be permitted to be replaced with another nongrounding-type receptacle(s).
(b) A nongrounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type
of receptacle(s). These receptacles shall be marked ?No Equipment Ground.? An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter- type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) A nongrounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked ?GFCI Protected? and ?No Equipment Ground.? An equipment grounding conductor shall not be connected between the grounding-type receptacles.
4.) Substantiation: There is currently no wording regarding additions to existing installations in 406.3(D). A Fine Print Note in 250.130(C) directs users of the NEC to 406.3(D) when applying the provisions of 250.130(C), but one of the scenarios outlined in 250.130(C) is overlooked: additions. Given the permissive nature of 250.130(C), an equipment grounding conductor (EGC) is permitted, but not required, to be installed for receptacle replacement.(D) Replacements. Replacement of receptacles and additions to existing branch circuits shall comply with 406.3(D)(1), (2), and (3) as applicable.
(1) --no change--
(2) --no change--
(3) Nongrounding-Type Receptacles. Where grounding means does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).
(a) A nongrounding-type receptacle(s) shall be permitted to be replaced with another nongrounding-type receptacle(s). Existing circuits that utilize nongrounding-type receptacles shall be permitted to supply an addition to such a circuit, where nongrounding-type receptacles are installed. An equipment grounding conductor shall not be connected between the nongrounding-type receptacles, or to any metallic enclosure in which they are installed.
(b) A nongrounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked ?No Equipment Ground.? An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any new or existing outlet or enclosure supplied from the ground-fault circuit-interrupter receptacle.
(c) A nongrounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles at new and existing locations supplied through the ground-fault circuit interrupter shall be marked ?GFCI Protected? and ?No Equipment Ground.? An equipment grounding conductor shall not be connected between the grounding-type receptacles, or to any metallic enclosure in which they are installed.
But there contains no language, permissive or otherwise, in relation to additions to existing circuits.
Users of the code looking to 250.130(C) when installing an addition to an existing circuit are advised by the FPN to see 406.3(D), but are left empty-handed when they get there.
The section in question (406.3(D)) effectively bends the standard requirements for new installations to provide relief for the installer when dealing with old work. Given the leniency put forth by this section regarding replacement receptacles, it appears that old 2-wire installations, while regretable, do not present an "imminent danger to occupants" as stated in 80.5(B).
80.5(C) expresses that "Additions...shall not cause a building to become unsafe..." By expressing explicit guidelines for additions to existing circuits, installers will be forbidden to connect an unbonded EGC between receptacles, decreasing the shock hazard in the event of an unbonded fault.
Whether accepted or declined, I hope this proposal causes the panel to adopt some definute wording, to fill the void on existing installations.