Re: Revise 406.3
The allowance of the circuit to be extended does not permit the installation of two-wire receptacles on the new portion of that circuit.
It expressly permits the extension and use of K&T, not the installation of a new nongrounding-type receptacle.
The receptacle would have to comply with 406.3, same as if I added romex to the circuit.
I don't think so.Originally posted by rbalex (and agreed upon by jw):
Therefore, 15 & 20A two-wire branch circuit extensions with non-grounding type receptacles are prohibited except as expressly permitted - such as with K&T ([2002]394.10).
The allowance of the circuit to be extended does not permit the installation of two-wire receptacles on the new portion of that circuit.
It expressly permits the extension and use of K&T, not the installation of a new nongrounding-type receptacle.
The receptacle would have to comply with 406.3, same as if I added romex to the circuit.