Re: Rigid vs. PVC for Service Entrance Mast
Bill I have some questions.
Why is that 3 conductor SE?
Why is there no supports on the PVC under the meter?
Is the SE run at as much of an angle as it looks in the top picture? (proving Noxx's point)
Here there is no requirement for protection below eight feet so it would be SE all the way.
I have never seen SE sleeved in raceway in this area, if the area was subject to damage we would use pipe all the way.
We would never use 3 wire ahead of the service disconnect on 120/240 single phase.