ron
- New York, 40.7514,-73.9925
Smoke detector installed above a suspended ceiling on the underside of the concrete slab above (approx 8' cavity) in corridors. To save $$$, the EC wants to mount the smoke detector on a 4"x4" box and attach the 4x4 box to a stick of 3/4" EMT which is bent such that it looks like a flag pole. The bend is placed so that when the vertical portion is held against the side wall above the suspended ceiling, the detector is located in the center of the corridor and against the underside of the concrete slab above. The bottom of the flag pole gets attached to the gyp board side wall above the suspended ceiling with two Minerallacs installed approx 6" apart beginning at the bottom of the "flagpole". Other than the two Minerallacs, the assembly is unsupported for the remainder of the vertical portion and the horizontal portion. The wire for the detector is wire tied to the side of the 3/4" conduit and enters the box through a grommet. The wire is not in the conduit so I can't say that the raceway is not supported per 358 because it is not raceway.
I think that the box support is not in compliance with 314.23(A) as the box it is not rigidly and securely fastened. The EC feels that he is in compliance with that article as he is following 314.23(B) and it does not require rigidly and securely, just rigidly. What does rigidly mean?
I am looking for opinions.
I think this is just a cheapie way of installing the device. The EC feels that he will save time, as he does not have to struggle above the deep cavity of the suspended ceiling and just raise the "flagpole" and attach to the wall near the susp ceiling elevation.