scottwnuwer
- Port Charlotte, FL
- Electrician
After Hurricane Milton, we are experiencing several homes along the coast that have had load centers/main breakers either just above, at, or below the level of flood waters.  Sometimes only the enclosure or cabinet received flooding (without submerging the load side wiring), and sometimes the bottom few breaker spaces on the busbar received flooding.  First, I would like to know thoughts on trying to salvage the busbar and main breaker if only the bottom of the enclosure received flooding.  Second, if the flood water did make it up to the few bottom breaker spaces, what is everyones thought on attempting to flush out the busbar and blow it out.  Almost all of the flood damaged equipment is copper tinned bus, and the enclosure is located on the gulf of Mexico anyways.  Typically the outdoor electrical enclosure only lasts 5-15 years anyways.  I read the NEMA article mentioning reconditioning of panelboards, which I imagine would require a recertification.  My thought is to flush out the enclosure, blow dry, hilco lube the connections, and recommend total replacement within 90 days.  It has only been a little over a week from the storm and most connections seem solid.  I only mention this possible approach because I am becoming overwhelmed with customers, and would like to provide a temporary solution to restore power so they can return home and live in the upstairs portion, and guarantee a panel change for the future.  Thoughts?