Granja
- Virgina Beach, VA, USA
My question concerns having a multi-pole breaker as a disconnecting means for multi-wire branch circuit that feeds roadway lighting. In this case, where a sequential line of poles/fixtures would be circuited with alternating phases (A, B & C - 277V line to neutral); Art 210.4(B) dictates that three line-to-neutral circuits must be protected by a 3-pole breaker instead of three separate single-pole breakers.This presents a dilema implementing the standard for circuiting with alternating phases.
With the single-pole breaker standard; when/if a breaker trips only every third fixture will extinguish, thereby enhancing public safety by keeping 2/3rds of the amount of light remaining for the roadway in a given sequence.
An example might be when a car hits a pole and potentially trips the 3-pole breaker, taking out the lights in 2500 ft sequence - thereby providing less light for emergency personnel, etc. It seems that there should be an exception to Art 210.4(B) for Roadway Lighting circuited in this fashion.
Otherwise, the municipality would have to endure the added cost for running separate neutral conductors and related costs.