1st time ever seeing this. Is this type generally approved? I am used to see more substantial means to accomplish this.
Hope that welding receptacle isn't used as a power inlet!
And what branch circuits are we transferring power to .... Don't see any.
While it does serve the purpose and I don't have an issue with using it, some inspectors will not permit it because 702.5 requires the use of "transfer equipment". The interlock device has all of the required functions of "transfer equipment" but is not listed as "transfer equipment". Check with your AHJ.
The rule in 702.5 requires the use of transfer equipment. There are no markings or other information that tells you the breaker interlock is transfer equipment. If it is not transfer equipment it does not meet the rule. Again, it has the functions of transfer equipment and many inspectors are ok with it, but some are not.I can't find where 705 says Transfer Equipment must be "listed" as such? (Unless it contains supplementary overcurrent protection)
The rule in 702.5 requires the use of transfer equipment. There are no markings or other information that tells you the breaker interlock is transfer equipment.
Sure looks like the receptacle is likely the standby power inlet to me.Hope that welding receptacle isn't used as a power inlet!
And what branch circuits are we transferring power to .... Don't see any.
My thoughts as well.I disagree with that.
The section does not require listed transfer equipment therefore anything that is designed to prevent the connection of both sources meets that code section.
Everything has to be "approved" per 110.2. A number of inspectors will not approve the use of the interlock as "transfer equipment".I disagree with that.
The section does not require listed transfer equipment therefore anything that is designed to prevent the connection of both sources meets that code section.
I understand that as well, doesn't mean I always agree with inspectors though.Everything has to be "approved" per 110.2. A number of inspectors will not approve the use of the interlock as "transfer equipment".
It may or may not be listed, it is not listed "transfer equipment".As already stated, check with your AHJ. The inspector I generally call (we have 3rd party inspection agencies) will approve an interlock provided it is listed for the particular brand breakers/panel it is installed in.
The one in the picture may or may not be listed for square D.
Sure looks like the receptacle is likely the standby power inlet to me.
What circuits are supplied, the left breaker is probably normal power input, the right breaker is probably standby input, the main lugs of the panelboard are supplying the load as they are the "common point" of the "transfer device"