Re: romax in conduit
Ebjur-what is the application? You can run 6-3 NM in a PVC raceway, you need to observe raceway fill per chapter 9, one conductor based on outer diameter of NM.
If by chance this is for a hot tub, NM cable is only allowed for installations on the interior of a single family dwelling. NM cable is not allowed in a PVC raceway underground for any application, the jacket is not water proof and the conductors inside are not rated for wet locations.