kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
now that the OP question was answered, the above in red won't fly unless you plan to run all #8x3 conductor or #6x2 conductor cable? anything smaller will be required through bored holes. see 334.15(C)
only if running them across the bottom of the joists he did not say where he was running them on the joists, parallel on the side of joist is a possibility.