I know this has likely been beaten to death, but I'm happy to bring it up again. Correct me if I'm wrong; romex(nm) wiring is limited to the 60 degree column in table 310.16. So a 60 amp hot tub's disconnect could not be fed with 6/3 romex, but the load side to the tub could be #6 THWN. It's my understanding that the insulation on romex is rated higher than 60 degrees, but because it's part of a cable assembly it is limited. The same way that SER is comprised of individual XHHW conductors, but because it's part of a cable assembly it too is limited to 60 degrees.
Hoping we can put this to rest (yeah right). I see a lot of electricians with many more years in the field than me purchasing 8/3 for a 50 amp circuit and 6/3 for a 60. I'm pretty certain I'm correct on the romex issue, but I'm a bit unsure on the SER issue.
Thanks in advance all!