In romex branch circuits. The outlet and switch boxes. Does it say in the NEC that the equipment ground wires have to be made up (twisted, wire nuted, connected ,etc....} for the rough-in inspection ?
It is often customary to do so.
not NEC required. Inspectors here like to see boxes made up at rough-in. Personally, I always do as much as mechanically possible prior to RI inspection so finish is quick and easy.