I have night dance club in which wiring method used is Romex cable. Is wiring method Romex cable permitted in this sort of commericial application per NEC 2014?
Until I read your post I thought you were talking about a bunch of electricians that only use Romex and get together for drinks once a week. :lol:
-Hal
Its a club. It is place of assembly about 90 person gather. Where do i find not allowed acoustic ceiling commeticial in nec and how do i know construction type?
Technically, you need to consider what construction type would be required under current code rather than what the actual construction type is.Ok it is assembly occupancy load is 102. So do i need to consider construction type?
Ok it is assembly occupancy load is 102. So do i need to consider construction type?
334.10 Uses Permitted. Type NM, Type NMC, and Type NMS
cables shall be permitted to be used in the following, except as
prohibited in 334.12:
(1) One- and two-family dwellings and their attached or
detached garages, and their storage buildings.
(2) Multi-family dwellings permitted to be of Types III, IV,
and V construction.
(3) Other structures permitted to be of Types III, IV, and V
construction. Cables shall be concealed within walls,
floors, or ceilings that provide a thermal barrier of material
that has at least a 15-minute finish rating as identified
in listings of fire-rated assemblies.
518.4 Wiring Methods.
(B) Nonrated Construction. In addition to the wiring methods
of 518.4(A), nonmetallic-sheathed cable, Type AC cable,
electrical nonmetallic tubing, and rigid nonmetallic conduit
shall be permitted to be installed in those buildings or portions
thereof that are not required to be of fire-rated construction by
the applicable building code.
Assembly with occupancy load 102 construction type II. So I can use Romex?
If it has an occupancy listed as 102 then it falls under code as a place of assembly and if I'm not mistaken romex(nm-b) is not allowed.
Very good..........Until I read your post I thought you were talking about a bunch of electricians that only use Romex and get together for drinks once a week. :lol:
-Hal
NM cable is allowed in an assembly occupancy in walls floors and ceilings that are non-rated construction.
See 518.4(B) that I quoted earlier.
Chris
I would NOT interpret that to allow use of NM in non-rated (if there is a way you could get them non-rated) walls erected in the middle of a rated occupancy.
I do see it as applying to a multiple use building with identifiable sections and to walls that are not part of a rated occupancy section.
Do you have AHJ experience to support your interpretation? If so, I am happy to be educated.
In other words, a wall which is not a boundary wall inside a rated occupancy may not have a specific fire rating assigned, but I would still not use NM in it.