mstrlucky74
Senior Member
- Location
- NJ
Now you're getting colder. 225A, 208V, 3ph is ~80,000KVA. In that space, you're not going to have 4 60A 3ph welders running simultaneously at a 100% duty cycle. You'd have 1 running some minutes here and there at ~30% or so. and you already wrote they are 1ph welders. 700ft sq is ~26 x 26, one or two welding receptacles would be fine. The other loads are all very minimal; hoists arent gonna run with 2 ton loads the entire day, lights for 700ft maybe a few kw if incandescent or halogen, and receptacles for tools, 3 20A breakers would cover it.
A 100A 1ph panel would be severe overkill here; 225A 3ph is like launching a nuke at a gnat.
lol....we might have a few welders running at the same time...maybe 2....I think the welding are 3P. The GC asked for 4 receptacles, doesn't say amperage or whether single or three phase.