Legal,no prohibition.
Get the NM cable from Canada; they have it with red and black, no white.
I call it DC Romex.
See: 210.5(C)(2), 250.162 and 250.164, 410.134, and solar if applicable.
Start at 690.31.How would you label it as a photovoltaic source?
Start at 690.31.
Sorry, I’m not seeing the argument that nm is allowed. It says it needs to be guarded or in a raceway.
Legal or not? Code reference if applicable.
So I read all the posts and if I read them correctly, the only approved flexible cable assembly for DC PV run is type MC?
Inside a building, if it is not otherwise inside a raceway, yes. DC circuits from solar arrays, have to be in metal, in some form or another. This would either mean using metal clad or armored cable, or using a metal raceway.
Outside within the array field on the racking, you do have other options for using a multiconductor cable, if it is either "guarded" by being not readily accessible or by being behind a locked fence. The cable you would use would have to be listed for use in a wet location, UV stable, and if your system is over 600V, it would also have to carry a special voltage rating. NM cable (e.g. Romex) meets none of these requirements.
690.31 Methods Permitted.
(A) Wiring Systems. All raceway and cable wiring methods included in this Code, other wiring systems and fittings specifically listed for use on PV arrays, and wiring as part of a listed system shall be permitted. Where wiring devices with integral enclosures are used, sufficient length of cable shall be provided to facilitate replacement.
Good info, this first job I’m doing is on my own home and getting a raceway from the array would be an absolute nightmare with windows doors and eaves in the way there is no elegant way to make a run however with a new roof penetration, I can easily intersect the path that my #4 is taking from the new panel to the water service.