romex for temp

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The NEC uses these definitions:

590.3 Time Constraints.
(A) During the Period of Construction. Temporary elec-
tric power and lighting installations shall be permitted dur-
ing the period of construction, remodeling, maintenance,
repair, or demolition of buildings, structures, equipment, or
similar activities.
(B) 90 Days. Temporary electric power and lighting instal-
lations shall be permitted for a period not to exceed 90 days
for holiday decorative lighting and similar purposes.
(C) Emergencies and Tests. Temporary electric power and
lighting installations shall be permitted during emergencies
and for tests, experiments, and developmental work.
(D) Removal. Temporary wiring shall be removed imme-
diately upon completion of construction or purpose for
which the wiring was installed.
 