jumper
Senior Member
- Location
- 3 Hr 2 Min from Winged Horses
Jumper,
This is a DIY. Don't even look at his EGC connection, thanks.
Protection is a good idea.
Running from a panel to a dedicated receptical, surface mounted in a garage, imagine that the Romex leaves the panel, up an inclosed wall, across the attic, entered conduit in the garage, down the wall to the Receptical.
I have been told I must transition from Romex, in a JB, and down with THHN.
I maintain that the code allows a continuous run of Romex
from the Breaker Box to the conduit and down to the Receptical.
and i maintain that you are right, np jb is necessary, 334.15c bushing or connector only .