Does is state in the 2008 NEC that you have to use UF cable to feed an outdoor fixture in a wet location? Thanks in advance, MR. S
Does is state in the 2008 NEC that you have to use UF cable to feed an outdoor fixture in a wet location? Thanks in advance, MR. S
Nowhere does it state you are required to use exclusively UF, as any wiring method approved for wet locations will suffice.
But NM cannot be used in a wet location. 334.12(B)(4).
I may learn the error in my ways, but, if you have a fixture installed outdoors in an unprotected area exposed to the weather, I think we all agree that is a wet location.
If that fixture is mounted to (or supplied from) a box mounted flush in the wall, then I see no problem NM supplyimg that box. Neither the box or the NM is exposed to the weather.
Whe I read the OP, this is what I pictured.
Does anyone look at the scenerio I mentioed in a different light ?
Does is state in the 2008 NEC that you have to use UF cable to feed an outdoor fixture in a wet location? Thanks in advance, MR. S
As usual, there is not enough information to determine an answer.
my question was answered, flush box romex, exterior box uf, or approved for wet location
By whom?
.........
Can you run uf in a pvc sleeve up the side of a house to the attic. Say 2 lbs and a stick of pipe? Just not nm.We have had this situation before where a box was mounted on the outside and it was fed by NM cable which at no point was ever exposed to the outside. It went from the inside directly to the back of the exterior box.
That is OK but if any part of the NM cable was visible on the outside then we have a problem.
Your issue is still not clarified. Maybe to you but maybe you are wrong.
Example: Someone in a thread on another forum thought at as long as you connected to any exterior box you had to use UF cable even though no part of it was ever visible or exposed to the elements.
Just trying to help a fellow EC such as yourself.
So if your basement is deemed a damp location, and you are into the 2008 NEC, all your wiring for the basement, and any feeds going thru the basement cannot be romex. $$$
So if your basement is deemed a damp location. . .
By whom?
.........
2 pounds?Can you run uf in a pvc sleeve up the side of a house to the attic. Say 2 lbs and a stick of pipe? Just not nm.
Can you run uf in a pvc sleeve up the side of a house to the attic. Say 2 lbs and a stick of pipe? Just not nm.
We do alot or most of the time run NM in pipe. When you have a homerun coming from an outside panel and have nowhere to splice from NM to THHN, what do you do? I have an example in the picture below. It is hard to see in the picture, but the panel next to the meter has a short piece of 2" PvC coming from the top of the panel into the soffit. Now, this PvC was installed to accomidate all needed homeruns for this dwelling.
According to code or from what a read as interpetation <sp> of the code, I am not allowed to run NM through this short piece of PvC due to the fact it is a wet or damp location.