SO; if I understand this correctly for my own future reference:
From NEC-2011
334.10 Uses Permitted.
Type NM, Type NMC, and Type NMS cables shall be permitted to be used in the following:
(3) Other structures permitted to be of types III, IV and V construction...Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.
Info-Note No.2 See Annex E for determination of building types [NFPA 220, Table 3-1]
Type V(000) is "wood frame" with non-rated (no fire-resistive requirements), which applies to this detached gazebo, which also allows some or all of the structural elements to be combustible (wood).
A wood tongue-in-groove ceiling in a wood gazebo permitted by the local building code sounds fine, but I am wondering about proving this 15-minute "thermal" barrier. Should be easy, right?
IBC-TABLE 721.6.2(1) TIME ASSIGNED TO WALLBOARD MEMBRANES
Includes an entry for: 19/32-inch wood structural panel bonded with exterior glue = 15 minutes
...but that appears to apply directly to walls, not to wood ceilings.
What I did not find through cursory review of online search results, was any 3rd-party certified test result chart of some code-accepted method to determine the fire-resistance rating of a wood ceiling of particular varieties (each tree is slightly different) with the "resistive membrane" (in this case T&G wood, of unknown type) directly applied to the exposed surface of the wood structural elements.
I found one independent report online at American Wood Council:
http://www.awc.org/pdf/WDF19-2_White.pdf
which listed a Table 1 showing a component-additive method that assigned a 15 minute resistive time to 5/8-inch thick Douglas-fir plywood, seemingly inline with the IBC wallboard time.
Surely a similar or thicker T&G (typically 3/4") would be as-resistive or better, without having to add insulation between the ceiling framing for additional fire-resistive ratings? Not specifically noted, but should be available from some reference somewhere, is the time assigned to UL "FR-S" rated wood products, or other "Fire Resistive Treated Lumber."
As an example, I found articles for "TimberSIL" - apparently some kind of silicate/glass-reinforced wood treatment, which can come in T&G panels - specifically tested as a rated Class A fire/ignition resistant ceiling decking approved in California for ceilings of outdoor patio structures in high fire vulnerability areas.
Does anyone else have a more specific easy-to-find PDF specifically stating "yep, any 5/8-inch or thicker T&G, (or maybe FR-treated 1/2-inch or thicker T&G, etc.) is a 15-minute thermal barrier that protects NM cabling from any further requirements"? :?