When using conduit to protect Romex before it enters an enclosure - for example, coming up out of the crawlspace, up an un-finished wall to a disconnect - what fastening requirements are recommended and/or required ?   (The conduit would run from the floor to the box).
What I've often done is to attach a female adapter to the far end of the conduit, and then screw an NM-B clamp into it. I suppose you could put the female adapter inside the enclosure (instead of the usual male adapter plus locknut, or box adapter) and use an NM-B clamp there - but it'd probably take up too much space.
I wonder if stapling the Romex within some distance of where it goes into the conduit is acceptable.
(Yes, I know you can't put Romex in conduit outdoors, unless you're a Tarheel and it's less than 6 ft).
	
		
			
		
		
	
				
			What I've often done is to attach a female adapter to the far end of the conduit, and then screw an NM-B clamp into it. I suppose you could put the female adapter inside the enclosure (instead of the usual male adapter plus locknut, or box adapter) and use an NM-B clamp there - but it'd probably take up too much space.